Working on a new site the last few weeks and its gained one of the worst maintained sites I have ever had to deal with. This is a point for point BMS replacement scope.

Last two days I had a small VAV system to fire up. 6 VAVs with HW and a two heat/cool VAV RTU. Figure I would start with the VAVs to make sure all the dampers are open before messing around with the RTU.

First VAV. Nothing special until I get to the checking the hot water valve. Some tiny JCI actuator on the valve I'm not familiar with but its clearly a 0-10v actuator. Step one, I need to sort out is 0v open or 10v open. Coil is valved off by the manual isolation valves. Rather inconvenient. Pull the actuator off, cycle the signal just to see if it even moves and it does. Linear action that pushes on the valve stem. Actuator works, still don't know which way is open. Decide to slowly open one of the isolation valves in series with the valve. Turns out the control valve was open and I can hear water going through. Second later its pouring out of the strainer someone left the cap off. Well that's kinda odd. For giggles I put the cap back on and slowly let the coil fill up. 15sec later, I can hear it leaking inside the duct. Well we must have a frozen / burst coil. Kinda a big blunder to have that happen. Whatever, close it back off and move to the next VAV, and the next, etc.

All six coils are valved off. Some with enough water damage to the tile, ceiling grid and drywall that its clear several of the coils have burst. Wow, large space and there is no secondary heat except for a stretch of fintube along the exterior walls. Go to check that valve, sure enough its also valved off. Not messing with that at this point.

Clearly something has gone seriously wrong with this system at some point. VAVs done, lets see what this RTU has to offer. Get to that, disconnect is off. Flip it on and the supply fan starts instantly. Seen this story already on every other unit that has a VFD on the roof. Open her up, yup more of the same. VFD failed, so it was replaced with three wire nuts and left as is. Now the full picture is coming into focus. That VFD bypass also bypasses the freezestat, smoke detector and any other safety in the unit. Its disconnect straight to the motor basically. Whatever, carry on. Well nothing in the unit is power up besides this fan. Turns out the control tranny is also burned out in the unit. Power for the course at this point. Hearing the air noise near the unit, have to wonder if the duct work is still intact. Enough of this, we're done.

End of the day finishing up silly UHs, CUHs, etc on small DDC controllers. Least 50% of them have one issue or another. Tons of them valved off. Wondering how the hell nothing freezes (well besides the VAV coils) and I get to the sprinkler / water main room and find this little guy protecting it from freezing. Yup, also valved off.
Sprinkler Room UH.jpg
Sprinkler Room UH.jpg (2.38 MiB) Viewed 56233 times
Every RTU with a VFD has failed and been bypassed with wire nuts except one. That one they installed a contactor in its place so it still follows a schedule. Bunch of unit vents in the building. Pipe insulation is torn up in many units, condensation of the CW lines is dripping on the econ, valve and F&B actuators. Least 50% of the units have at least one failed actuator.

Total dumpster fire. One of the worst off memory.
User avatar
orion242
Posts: 232
Joined: Fri Feb 21, 2020 12:55 am
Location: New England
Contact:

Re: Maintenace Program, or lack of

Post by orion242 »

Going through my camera roll, more pics got squirreled away in my personal WOS archive. Few more to share here.


Wire nut sales wet dream. This is prior factory control removal. Got'r'done I guess. Thanks for the labels on the RIBs. Cut above!
Wire nut sales wet dream.jpg
Wire nut sales wet dream.jpg (3.15 MiB) Viewed 56229 times
VFD Replacements
VFD Replacement 1.jpg
VFD Replacement 1.jpg (1.49 MiB) Viewed 56229 times
VFD Replacement 2.jpg
VFD Replacement 2.jpg (2.55 MiB) Viewed 56229 times
Airflow stations doing "DCV" first one is a 2 position OA actuator, second is at least modulating. Crappy pickup wire tied to the bird screen in all cases to a bog standard DP sensor.
AFMS on 2 pos actuator.jpg
AFMS on 2 pos actuator.jpg (2.62 MiB) Viewed 56229 times
Besides the AFMS, note the top damper blade. Its broken off on one end jamming up the whole economizer on this unit.
AFMS modulating actuator.jpg
AFMS modulating actuator.jpg (2.61 MiB) Viewed 56229 times
Attachments
Condsation on actuators.jpg
Condsation on actuators.jpg (2.29 MiB) Viewed 56229 times
User avatar
Maxburn
Posts: 101
Joined: Wed Mar 04, 2020 12:51 am

Re: Maintenace Program, or lack of

Post by Maxburn »

That takeover pic is rough, it would have actually been easier to switch to DIN and have a rack of relays and spade crimp connectors.
User avatar
orion242
Posts: 232
Joined: Fri Feb 21, 2020 12:55 am
Location: New England
Contact:

Re: Maintenace Program, or lack of

Post by orion242 »

Yea. Something tells me the installing contractor asked a few questions and the control outfit said...That's what on our drawings and what we supplied. Use it.