Engineer fails

Post Reply
User avatar
Maxburn
Posts: 97
Joined: Wed Mar 04, 2020 12:51 am

Engineer fails

Post by Maxburn »

Three 800 ton chillers feeding these three towers. Sequence calls for rotating the towers. Another paragraph of the sequence a bit later calls for modulating bypass to maintain CW temp during cold season. Somehow these two things never got put together, then it was built and now it will never get put together. My suggestion in red came in far too late and engineer changed the sequence to use tower 3 as primary. Now customer must deal with tower 1 and 2 turning into a swamp.

JustTowerssug.png
JustTowerssug.png (50.82 KiB) Viewed 4904 times
JustLegend.png
JustLegend.png (69.47 KiB) Viewed 4904 times
Post Reply